OK - a little homework here:
NFPA 99 2005 Chapter #1
Section 1.1.1 - Clearing state's (services to human being)
Section 1.3.1 - This document shall apply to all health care facilities.
(i.e. for human being)
But:
NFPA 99 2012 Chapter #1 Section 1.1 Throws in the full sections of 1.1.2 - 1.1.13
( no big deal here )
Section 1.3.1 - This document shall apply to all health care facilities other than home care.
(i.e. without the wording human being / its all lawyer talk / it's a document for fire protection right and not that long along a HBO center for horses blew up / public safety)
BUT AGAIN WE HAVE
NFPA 99 2015 Chapter #1 Section 1.1 Throws in the full sections of 1.1.2 - 1.1.13
( no big deal here again )
Section 1.3.1 - This document shall apply to all health care facilities other than home care and veterinary care.
(i.e. now we back to human being)
Even with all that, I like to quote Section#5.1.3.5.2
Permitted Locations for Medical Gases.
Which applies to.
The Central Supply Systems
(i.e. the Bulk Oxygen Site)
You should and in my opinion, cannot share this bulk oxygen site
for your stated purpose.
Just like you cannot use, a healthcare facility bulk oxygen site for transfilling homecare liquid vessels.